[{"data":1,"prerenderedAt":-1},["ShallowReactive",2],{"topic-8321":3},{"id":4,"firstPostId":5,"title":6,"author":7,"date":14,"lastReply":15,"category":16,"tags":17,"isFeatured":19,"isSticky":19,"isLocked":19,"isResolved":19,"isExpertInvited":19,"bestAnswerPostId":13,"canSticky":19,"canLock":19,"commentsCount":20,"lastPostNumber":21,"lastReadPostNumber":13,"hasNewMessages":19,"unreadCount":22,"views":23,"subscribersCount":21,"isSubscribed":19,"userVote":22,"votesCount":22,"bodyHtml":24,"rawContent":25,"rawCreatedAt":26,"rawLastPostedAt":27,"answers":28},8321,37271,"Какие требования к дверям в производственном помещении?",{"id":8,"username":9,"name":10,"initials":11,"color":12,"avatarUrl":13,"groupBadge":13},"559","3592681176701952779","Lesya","LE","#047857",null,"1 сент. 2023 г.","3 сент. 2023 г.","Пожарная безопасность",[16,18],"обязательные требования",false,7,8,0,946,"\u003Cp>Производственное помещение (кабинеты, место отдыха, санузел) площадь около 200 кв.м., нужна ли противопожарная дверь на выходе в фойе или можно поставить пластиковую?\u003C\u002Fp> ","Производственное помещение (кабинеты, место отдыха, санузел) площадь около 200 кв.м., нужна ли противопожарная дверь на выходе в фойе или можно поставить пластиковую?","2023-09-01T08:45:04+00:00","2023-09-03T20:12:27+00:00",[29,45,66,81,121,136,151],{"id":30,"number":31,"author":32,"date":14,"isSolution":19,"text":39,"rawContent":40,"votes":22,"userVote":22,"canFlag":19,"canVote":19,"canEdit":19,"canDelete":19,"isEditing":19,"reactions":41,"reactionUsers":42,"reactedEmoji":13,"comments":43,"isCommentsOpen":19,"rawCreatedAt":44},37279,2,{"id":33,"username":34,"name":35,"initials":36,"color":37,"avatarUrl":38,"groupBadge":13},"80","zhurtov","Алим Хасанович","АХ","#BE123C","\u002Fassets\u002Favatars\u002FkcLqDwztoYDg97e4.png","\u003Cblockquote class=\"uncited\">\u003Cdiv>\u003Cp>\u003Ca href=\"\u002Fquestion\u002F8321#post-1\" class=\"PostMention post-mention-tag\" data-id=\"37271\" rel=\"\" target=\"\">\u003Cspan class=\"mention-reply-arrow\" title=\"Перейти к сообщению\">⮑\u003C\u002Fspan> \u003Cspan class=\"mention-author-name\" title=\"Карточка специалиста SpecHelp ID\">Lesya\u003C\u002Fspan>\u003C\u002Fa> Производственное помещение (кабинеты, место отдыха, санузел) площадь около 200 кв.м., нужна ли противопожарная дверь на выходе в фойе или можно поставить пластиковую?\u003C\u002Fp>\u003C\u002Fdiv>\u003C\u002Fblockquote>\u003Cp>Вот когда откроете проект вашего здания, в частности места фойе и там по проекту была заложена дверь противопожарная, а значит отсекающая горение с одной комнаты на другую, то НУЖНА!\u003Cbr>\u003Cbr>В противнм сд\\лучае, нет!\u003C\u002Fp>","[Lesya](http:\u002F\u002F185.104.248.233\u002Fd\u002F8321\u002F1) Производственное помещение (кабинеты, место отдыха, санузел) площадь около 200 кв.м., нужна ли противопожарная дверь на выходе в фойе или можно поставить пластиковую?\n\nВот когда откроете проект вашего здания, в частности места фойе и там по проекту была заложена дверь противопожарная, а значит отсекающая горение с одной комнаты на другую, то НУЖНА!\n\nВ противнм сд\\лучае, нет!",{},{},[],"2023-09-01T09:10:34+00:00",{"id":46,"number":47,"author":48,"date":14,"isSolution":19,"text":60,"rawContent":61,"votes":22,"userVote":22,"canFlag":19,"canVote":19,"canEdit":19,"canDelete":19,"isEditing":19,"reactions":62,"reactionUsers":63,"reactedEmoji":13,"comments":64,"isCommentsOpen":19,"rawCreatedAt":65},37280,3,{"id":49,"username":50,"name":51,"initials":52,"color":53,"avatarUrl":54,"groupBadge":55},"1192","olka","Olka","OL","#1D4ED8","\u002Fassets\u002Favatars\u002F3vgfKuwEmClvH9uj.png",{"id":56,"name":57,"icon":58,"color":59},5,"Эксперт","fas fa-star","#287b32","\u003Cp>Поддерживаю коллегу. ФЗ-123 Статья 88. Требования к ограничению распространения пожара в зданиях, сооружениях, пожарных отсеках в помощь.\u003C\u002Fp>","Поддерживаю коллегу. ФЗ-123 Статья 88. Требования к ограничению распространения пожара в зданиях, сооружениях, пожарных отсеках в помощь.",{},{},[],"2023-09-01T09:12:38+00:00",{"id":67,"number":68,"author":69,"date":14,"isSolution":19,"text":75,"rawContent":76,"votes":22,"userVote":22,"canFlag":19,"canVote":19,"canEdit":19,"canDelete":19,"isEditing":19,"reactions":77,"reactionUsers":78,"reactedEmoji":13,"comments":79,"isCommentsOpen":19,"rawCreatedAt":80},37290,4,{"id":70,"username":71,"name":72,"initials":73,"color":74,"avatarUrl":13,"groupBadge":13},"4458","15457763141500850146","Алексей","АЛ","#4338CA","\u003Cp>Думаю, что необходимо  исходить от проектной документы и классов функциональной пожарной опасности помещений. Руководствоваться дополнительно основным ФЗ №123 и приказом МЧС России от 14.02.2020 № 89.\u003C\u002Fp>","Думаю, что необходимо  исходить от проектной документы и классов функциональной пожарной опасности помещений. Руководствоваться дополнительно основным ФЗ №123 и приказом МЧС России от 14.02.2020 № 89.",{},{},[],"2023-09-01T09:59:32+00:00",{"id":82,"number":56,"author":83,"date":14,"isSolution":19,"text":90,"rawContent":91,"votes":22,"userVote":22,"canFlag":19,"canVote":19,"canEdit":19,"canDelete":19,"isEditing":19,"reactions":92,"reactionUsers":93,"reactedEmoji":13,"comments":94,"isCommentsOpen":19,"rawCreatedAt":120},37295,{"id":84,"username":85,"name":86,"initials":87,"color":37,"avatarUrl":88,"groupBadge":89},"2719","shevchenko","Rostov161","RO","\u002Fassets\u002Favatars\u002FKr0fjsBpMVTBq19HekWHImwY.png",{"id":56,"name":57,"icon":58,"color":59},"\u003Cp>Больше чем уверен, что по проекту будет противопожарная дверь))\u003C\u002Fp>","Больше чем уверен, что по проекту будет противопожарная дверь))",{},{},[95,107,114],{"id":96,"parentId":13,"author":97,"date":14,"text":104,"rawContent":105,"canEdit":19,"canDelete":19,"votes":31,"userVote":22,"reactions":106,"reactedEmoji":13},15818,{"id":98,"username":99,"name":100,"initials":101,"color":102,"avatarUrl":103,"groupBadge":13},"416","Change","Сергей Пронин","СП","#0369A1","\u002Fassets\u002Favatars\u002FWoEQyWXdktngPIiP6Ot5BJqT.png","\u003Cp>Больше уверен, что проекта нет)\u003C\u002Fp>","Больше уверен, что проекта нет)",{},{"id":108,"parentId":13,"author":109,"date":14,"text":111,"rawContent":112,"canEdit":19,"canDelete":19,"votes":22,"userVote":22,"reactions":113,"reactedEmoji":13},15819,{"id":84,"username":85,"name":86,"initials":87,"color":37,"avatarUrl":88,"groupBadge":110},{"id":56,"name":57,"icon":58,"color":59},"\u003Cp>Верно подмечено))))\u003C\u002Fp>","Верно подмечено))))",{},{"id":115,"parentId":13,"author":116,"date":14,"text":117,"rawContent":118,"canEdit":19,"canDelete":19,"votes":22,"userVote":22,"reactions":119,"reactedEmoji":13},15820,{"id":33,"username":34,"name":35,"initials":36,"color":37,"avatarUrl":38,"groupBadge":13},"\u003Cp>Больше чем уверен, что ни проекта, ни двери ещё долго не будет...\u003C\u002Fp>","Больше чем уверен, что ни проекта, ни двери ещё долго не будет...",{},"2023-09-01T10:20:05+00:00",{"id":122,"number":123,"author":124,"date":14,"isSolution":19,"text":130,"rawContent":131,"votes":22,"userVote":22,"canFlag":19,"canVote":19,"canEdit":19,"canDelete":19,"isEditing":19,"reactions":132,"reactionUsers":133,"reactedEmoji":13,"comments":134,"isCommentsOpen":19,"rawCreatedAt":135},37296,6,{"id":125,"username":126,"name":127,"initials":128,"color":129,"avatarUrl":13,"groupBadge":13},"3008","26630218513973910344","Marin","MA","#B91C1C","\u003Cblockquote class=\"uncited\">\u003Cdiv>\u003Cp>\u003Ca href=\"\u002Fquestion\u002F8321#post-1\" class=\"PostMention post-mention-tag\" data-id=\"37271\" rel=\"\" target=\"\">\u003Cspan class=\"mention-reply-arrow\" title=\"Перейти к сообщению\">⮑\u003C\u002Fspan> \u003Cspan class=\"mention-author-name\" title=\"Карточка специалиста SpecHelp ID\">Lesya\u003C\u002Fspan>\u003C\u002Fa> кабинеты, место отдыха, санузел\u003C\u002Fp>\u003C\u002Fdiv>\u003C\u002Fblockquote>\u003Cp>Ничего из этого не является производственным помещением. Вы уверены в определений класса функциональной опасности?\u003Cbr>\u003Cbr>Если все-таки Ф5, то еще потребуется определить категорию по взрывопожарной и пожарной опасности.\u003Cbr>\u003Cbr>Если проекта нет, то да - СП4.13130 в помощь.\u003C\u002Fp>","[Lesya](http:\u002F\u002F185.104.248.233\u002Fd\u002F8321\u002F1) кабинеты, место отдыха, санузел\n\nНичего из этого не является производственным помещением. Вы уверены в определений класса функциональной опасности?\n\nЕсли все-таки Ф5, то еще потребуется определить категорию по взрывопожарной и пожарной опасности.\n\nЕсли проекта нет, то да - СП4.13130 в помощь.",{},{},[],"2023-09-01T10:33:57+00:00",{"id":137,"number":20,"author":138,"date":15,"isSolution":19,"text":145,"rawContent":146,"votes":22,"userVote":22,"canFlag":19,"canVote":19,"canEdit":19,"canDelete":19,"isEditing":19,"reactions":147,"reactionUsers":148,"reactedEmoji":13,"comments":149,"isCommentsOpen":19,"rawCreatedAt":150},37352,{"id":139,"username":140,"name":141,"initials":142,"color":102,"avatarUrl":143,"groupBadge":144},"2785","minailov","_RosSia","_R","\u002Fassets\u002Favatars\u002FFUGsd2G81vOsDsLD.png",{"id":56,"name":57,"icon":58,"color":59},"\u003Cp>Лучше с проекта начать поиски, есть вообще ли...\u003C\u002Fp>","Лучше с проекта начать поиски, есть вообще ли...",{},{},[],"2023-09-03T14:22:00+00:00",{"id":152,"number":21,"author":153,"date":15,"isSolution":19,"text":160,"rawContent":161,"votes":22,"userVote":22,"canFlag":19,"canVote":19,"canEdit":19,"canDelete":19,"isEditing":19,"reactions":162,"reactionUsers":163,"reactedEmoji":13,"comments":164,"isCommentsOpen":19,"rawCreatedAt":27},37356,{"id":154,"username":155,"name":156,"initials":157,"color":129,"avatarUrl":158,"groupBadge":159},"425","smirnov","Sergey","SE","\u002Fassets\u002Favatars\u002FESlleolEd2ONK8ZA.png",{"id":56,"name":57,"icon":58,"color":59},"\u003Cp>\u003Ca href=\"\u002Fquestion\u002F8321#post-1\" class=\"PostMention post-mention-tag\" data-id=\"37271\" rel=\"\" target=\"\">\u003Cspan class=\"mention-reply-arrow\" title=\"Перейти к сообщению\">⮑\u003C\u002Fspan> \u003Cspan class=\"mention-author-name\" title=\"Карточка специалиста SpecHelp ID\">Lesya\u003C\u002Fspan>\u003C\u002Fa> Здравствуйте. В число базовых документов, регламентирующих правила установки противопожарных дверей, входит Технический регламент о требованиях пожарной безопасности. Он введен в действие Федеральным законом №123-ФЗ. Серьезное влияние на уровень и количество требований к установке противопожарных дверей оказывает функциональное назначение зданий и помещений, на входе в которые они монтируются.\u003Cbr>\u003Cbr>\u003Cstrong>Лестничные клетки и лифтовые холлы\u003C\u002Fstrong>\u003Cbr>\u003Cbr>Необходимость установки противопожарных дверей на входах в лестничные клетки и лифтовые холлы легко объяснима. Дело в том, что указанные части здания в обязательном порядке используются для эвакуации людей.\u003Cbr>\u003Cbr>\u003Cstrong>Электрощитовые\u003C\u002Fstrong>\u003Cbr>\u003Cbr>Работоспособность системы электроснабжения здания выступает одним из обязательных условий для проведения оперативной эвакуации людей и эффективного использования лифтов, систем дымоудаления и пожаротушения, а также других инженерных сетей. Поэтому на входе в электрощитовые, отвечающие за исправное энергообеспечение постройки, обязательно устанавливаются противопожарные двери.\u003Cbr>\u003Cbr>Требования к ним определятся по схеме, описанной выше для лестничных клеток и лифтовых холлов. Они зависят от назначения постройки, площади электрощитовой и других подобных параметров.\u003Cbr>\u003Cbr>\u003Cstrong>Складские помещения\u003C\u002Fstrong>\u003Cbr>\u003Cbr>Необходимость установки противопожарных дверных конструкций на входе в складские помещения определяется в зависимости от вида и характеристик товаров, веществ и материалов, хранящихся внутри. В зависимости от этого параметра все объекты делятся на несколько категорий:\u003Cbr>\u003Cbr>«А» - складские помещения с повышенной взрывопожароопасностью. Пример – станции для хранения легковоспламеняющихся жидкостей, аккумуляторные установки стационарного типа и т.д.;\u003Cbr>\u003Cbr>«Б» - взрывопожароопасные склады (цеха по изготовлению древесной муки, станции по производству дизельного топлива);\u003Cbr>\u003Cbr>«В» - пожароопасные помещения. Делятся на 4 группы – от В1 до В4. Примеры – торфяные хранилища, автомастерские, трансформаторные подстанции и подобные постройки;\u003Cbr>\u003Cbr>«Г» и «Д» - склады с умеренным и пониженным уровнем пожароопасности.\u003Cbr>\u003Cbr>Для складских и производственных помещений первых трех категорий предусматриваются повышенные требования противопожарной безопасности. Одно из них – установка огнестойких дверей. Минимальные характеристики конструкций определяются в зависимости от параметров конкретного здания. Например, для складов категории В3 и В4 требуется монтаж противопожарных дверей с пределом огнестойкости не менее 30 минут.\u003Cbr>\u003Cbr>\u003Cstrong>Пути эвакуации\u003C\u002Fstrong>\u003Cbr>\u003Cbr>Монтаж огнестойких дверей на путях эвакуации любых построек, которые относятся к местам массового скопления людей – одно из обязательных правил в области пожарной безопасности. К подобным конструкциям предъявляются стандартные требования, в числе которых:\u003C\u002Fp>\u003Cul>\u003Cli>открывание по направлению движения людей к эвакуационному выходу из здания;\u003C\u002Fli>\u003Cli>минимальные габариты – ширина от 80 см и высота от 190 см;\u003C\u002Fli>\u003Cli>предел огнестойкости – 30 минут и выше.\u003C\u002Fli>\u003C\u002Ful>\u003Cp>\u003Cstrong>Важно.\u003C\u002Fstrong> Конкретный набор эксплуатационных и противопожарных характеристик дверей определяется на стадии проектирования здания. Он зависит от функционального назначения постройки, этажности и площади, а также других подобных факторов.\u003C\u002Fp>","[Lesya](http:\u002F\u002F185.104.248.233\u002Fd\u002F8321\u002F1) Здравствуйте. В число базовых документов, регламентирующих правила установки противопожарных дверей, входит Технический регламент о требованиях пожарной безопасности. Он введен в действие Федеральным законом №123-ФЗ. Серьезное влияние на уровень и количество требований к установке противопожарных дверей оказывает функциональное назначение зданий и помещений, на входе в которые они монтируются.\n\n**Лестничные клетки и лифтовые холлы**\n\nНеобходимость установки противопожарных дверей на входах в лестничные клетки и лифтовые холлы легко объяснима. Дело в том, что указанные части здания в обязательном порядке используются для эвакуации людей.\n\n**Электрощитовые**\n\nРаботоспособность системы электроснабжения здания выступает одним из обязательных условий для проведения оперативной эвакуации людей и эффективного использования лифтов, систем дымоудаления и пожаротушения, а также других инженерных сетей. Поэтому на входе в электрощитовые, отвечающие за исправное энергообеспечение постройки, обязательно устанавливаются противопожарные двери.\n\nТребования к ним определятся по схеме, описанной выше для лестничных клеток и лифтовых холлов. Они зависят от назначения постройки, площади электрощитовой и других подобных параметров.\n\n**Складские помещения**\n\nНеобходимость установки противопожарных дверных конструкций на входе в складские помещения определяется в зависимости от вида и характеристик товаров, веществ и материалов, хранящихся внутри. В зависимости от этого параметра все объекты делятся на несколько категорий:\n\n«А» - складские помещения с повышенной взрывопожароопасностью. Пример – станции для хранения легковоспламеняющихся жидкостей, аккумуляторные установки стационарного типа и т.д.;\n\n«Б» - взрывопожароопасные склады (цеха по изготовлению древесной муки, станции по производству дизельного топлива);\n\n«В» - пожароопасные помещения. Делятся на 4 группы – от В1 до В4. Примеры – торфяные хранилища, автомастерские, трансформаторные подстанции и подобные постройки;\n\n«Г» и «Д» - склады с умеренным и пониженным уровнем пожароопасности.\n\nДля складских и производственных помещений первых трех категорий предусматриваются повышенные требования противопожарной безопасности. Одно из них – установка огнестойких дверей. Минимальные характеристики конструкций определяются в зависимости от параметров конкретного здания. Например, для складов категории В3 и В4 требуется монтаж противопожарных дверей с пределом огнестойкости не менее 30 минут.\n\n**Пути эвакуации**\n\nМонтаж огнестойких дверей на путях эвакуации любых построек, которые относятся к местам массового скопления людей – одно из обязательных правил в области пожарной безопасности. К подобным конструкциям предъявляются стандартные требования, в числе которых:\nоткрывание по направлению движения людей к эвакуационному выходу из здания;\nминимальные габариты – ширина от 80 см и высота от 190 см;\nпредел огнестойкости – 30 минут и выше.\n\n**Важно.** Конкретный набор эксплуатационных и противопожарных характеристик дверей определяется на стадии проектирования здания. Он зависит от функционального назначения постройки, этажности и площади, а также других подобных факторов.",{},{},[]]